Currently looking for a cheap AC unit on Craigslist, I figured now would be as good as time as ever with summer just ending. I only have $80, hopefully I'll be able to score something. I know we have a igloo cooler in our garage, not sure if my dad will let me hack it up though
.
Have any of you tried running your chillers outside during the winter? I was wondering if they still worked, I know that the gases they use rely on certain ambient temperatures in order for the gas to change phases properly. I was curious to see if they still worked, It would be nice to be able to get evap that much colder.
No its a very bad idea to run a refrigeration system at that low of a condensing temperature.
typically units that are run in the winter use a "
head pressure control" essentially it just shuts off the condensor fan to allow the condensing temperature/pressure to rise to an acceptable level.
The problem is that at low temp, lower pressure is required for the refrigerant to condense from vapor into the liquid,
this in turn will massively reduce the cooling capacity of a unit, as you have now decreased the actual amount of refrigerant traveling through the metering device(captube,txv, etc...)
this will result in poor metering,reduced capacity, and possibly overheating of the compressor, remember the compressor is cooled by the returning evaporated refrigerant vapor, decrease that and BAD things happen.
and NO, running the unit outside in the winter will not yield lower temperatures, because ...again you have reduced the liquid refrigerant pressure.
I hope I explained this properly, I haven't had my cup of coffee yet and am kinda sleepy still.